This site is not affiliated with AGCO Inc., Duluth GA., Allis-Chalmers Co., Milwaukee, WI., or any surviving or related corporate entity. All trademarks remain the property of their respective owners. All information presented herein should be considered the result of an un-moderated public forum with no responsibility for its accuracy or usability assumed by the users and sponsors of this site or any corporate entity.
The Forum Parts and Services Unofficial Allis Store Tractor Shows Serial Numbers History
Forum Home Forum Home > Other Topics > Shops, Barns, Varmints, and Trucks
  New Posts New Posts
  FAQ FAQ  Forum Search   Events   Register Register  Login Login


Water temp for heated floor.

 Post Reply Post Reply Page  12>
Author
Message
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Topic: Water temp for heated floor.
    Posted: 30 Nov 2024 at 8:02am
I have two connected pole barns that share a Navia on demand water heater. One building has an overhead box heater with radiator, fan, and louvers. The other building has tubes in the cement radiant heat.
The floor heat is off. The overhead box has been keeping both shops warm with 150 degree water. Last night it was colder and the OH box didn’t keep up.
What is my more efficient option? I can raise the water temp to the OH box (180?) or drop the water temp so I can run both heaters as the floor can only take 120 or so.

Back to Top
Sponsored Links


Back to Top
jaybmiller View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: Greensville,Ont
Points: 24335
Post Options Post Options   Thanks (0) Thanks(0)   Quote jaybmiller Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 8:44am
heat the floor.
hot water heats concrete, huge 'thermal mass' and warm air rises.
it'd be interesting to know what the temp leaving the overhead is.
say 150 going in and 120 coming out.... you could plumb to go IN the floor......
even if 80, I'd still try it......
3 D-14s,A-C forklift, B-112
Kubota BX23S lil' TOOT( The Other Orange Tractor)

Never burn your bridges, unless you can walk on water
Back to Top
DMiller View Drop Down
Orange Level Access
Orange Level Access


Joined: 14 Sep 2009
Location: Hermann, Mo
Points: 33121
Post Options Post Options   Thanks (0) Thanks(0)   Quote DMiller Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 10:40am
140 was the magic number I was explained as to spalling Concrete or causing cracking.
Back to Top
plummerscarin View Drop Down
Orange Level Access
Orange Level Access


Joined: 22 Jun 2015
Location: ia
Points: 3755
Post Options Post Options   Thanks (0) Thanks(0)   Quote plummerscarin Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 12:04pm
Were it me, I'd heat the floor. I don't fully understand your set up. Two buildings, connected. A wall separates the 2? No wall? Two heating methods. The floor system operates at a lower temperature but this is a set it forget it method. The overhead blower can operate off a programmable thermostat because it can raise and lower room temperature more quickly. My solution is a mixing valve on the radiant with water and thermostat at a lower temp. Operate the boiler at a higher temperature and a separate thermostat to raise and lower room temperature above fixed radiant temperature as desired.
Back to Top
DonBC View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 12 Sep 2009
Location: Courtenay, BC,
Points: 930
Post Options Post Options   Thanks (1) Thanks(1)   Quote DonBC Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 1:00pm
There are different systems for different purposes. Insulated building with constant use a heated floor works as well as forced air or a furnace.  For an uninsulated building and intermittent use it is best to use radiant heat as it heats the objects (you) quickly.
Back to Top
tadams(OH) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 17 Sep 2009
Location: Jeromesville, O
Points: 10609
Post Options Post Options   Thanks (0) Thanks(0)   Quote tadams(OH) Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 2:28pm
Heat rises and cold falls, I would keep the floor heated so it doesn't freez the pipes and have fans to circulate the heat from above.
Back to Top
steve(ill) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 11 Sep 2009
Location: illinois
Points: 85476
Post Options Post Options   Thanks (0) Thanks(0)   Quote steve(ill) Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 3:37pm
set the boiler at 120 degrees. The floor heat will work great and do 50% of the buildings.. The 120 degree water in the radiator heater for the other building should heat that 50% to an acceptable temp.
Like them all, but love the "B"s.
Back to Top
jaybmiller View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: Greensville,Ont
Points: 24335
Post Options Post Options   Thanks (0) Thanks(0)   Quote jaybmiller Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 3:52pm
hmm. share a Navia on demand water heater.

so WHERE is the thermostat placed ?
when I did remote energy control systems, each building had 'zones'( 1-6 space heaters), with their own thermostats.
In your case, you have two pole barns so two 'zones'...... each should have it's own stat and valving., PLUS the floor... so minimum of 3 zones.
3 D-14s,A-C forklift, B-112
Kubota BX23S lil' TOOT( The Other Orange Tractor)

Never burn your bridges, unless you can walk on water
Back to Top
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 7:34pm
Ok I need to be more clear. The two buildings have a shared 30 ft wall and a 10x10 door. The old 10’ side, fully insulated, has the overhead box heater.
The 14’ side, also insulated, has the heated floor.
With the door open between the two the overhead heater has been keeping up with both sides until today.
I tried turning up the water temp today but it seems the OH box is struggling to maintain temp.
I am trying to be as efficient as possible. My options appear to be turn the temp up for just the OH box or lower the temp and put on the floor to help the box. The above suggestion of a mixing valve is what I need. The OH box is nice with 172 degree water going in and at that temp the return temp shows 154.
I’ve sat here and decided to drop the WH temp and put the floor on with the thermostat set at 62 and see what that gets me.

Back to Top
steve(ill) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 11 Sep 2009
Location: illinois
Points: 85476
Post Options Post Options   Thanks (0) Thanks(0)   Quote steve(ill) Quote  Post ReplyReply Direct Link To This Post Posted: 30 Nov 2024 at 7:48pm
  I’ve sat here and decided to drop the WH temp and put the floor on with the thermostat set at 62 and see what that gets me.   Thumbs Up

We dont know the size of the radiator or the size of the fan pushing the air...  Right now you have a drop of 20 degrees ( 170 - 150 ) for the water and your raising the air temp a given amount as it blows over the radiator... It is POSSIBLE that if you set the water at 120 and get the 20 degree drop to 100 degrees, that you will STILL TRANSFER the same amount of heat to the air ... not a guarantee, but very possible not knowing the radiator or fan size... Its not the TEMP, its the DROP across the radiator that counts.. That could be why you see no difference when you raise the water up from 150 degrees... your still getting a 20 degree drop..


Edited by steve(ill) - 30 Nov 2024 at 8:00pm
Like them all, but love the "B"s.
Back to Top
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Posted: 01 Dec 2024 at 6:03am
I put the floor at 62 and the OH box at 66 and the floor didnt turn on because the ‘floor side’ thermostat was still reading the 66 degrees the box had been providing.
I left it with both box and floor both set at 66 when I came in. I will check the return temp when I go out. Hopefully there is more than 20 degrees of temp drop.
Thinking about a mixing valve…. If the OH box is putting out hotter air than the floor thermostat is set to the floor would not turn on unless I had the door between buildings closed.


Back to Top
plummerscarin View Drop Down
Orange Level Access
Orange Level Access


Joined: 22 Jun 2015
Location: ia
Points: 3755
Post Options Post Options   Thanks (0) Thanks(0)   Quote plummerscarin Quote  Post ReplyReply Direct Link To This Post Posted: 01 Dec 2024 at 6:17am
Is this a new heating system?
Back to Top
jaybmiller View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: Greensville,Ont
Points: 24335
Post Options Post Options   Thanks (0) Thanks(0)   Quote jaybmiller Quote  Post ReplyReply Direct Link To This Post Posted: 01 Dec 2024 at 6:25am
Normally the floor stat is IN the concrete floor,several feet from the edge, so I'm curious as to where the stats are. I'll assume the OH furnace's  stat is 5' off the floor ,underneath the  OH ?
Each OH should have it's own stat and valve, same for the floor. Done like this ,it's easy to get very good control.I used to do this for 40-50 medium sized businesses in Hamilton area here, 3 decades ago. saved them 30%+ of their heating costs.
3 D-14s,A-C forklift, B-112
Kubota BX23S lil' TOOT( The Other Orange Tractor)

Never burn your bridges, unless you can walk on water
Back to Top
steve(ill) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 11 Sep 2009
Location: illinois
Points: 85476
Post Options Post Options   Thanks (0) Thanks(0)   Quote steve(ill) Quote  Post ReplyReply Direct Link To This Post Posted: 01 Dec 2024 at 8:19am
i think Jay is right... your FLOOR thermostat needs to be in the floor or TOUCHING the flloor or at the FAR END of that building if mounted on the wall.. If its reading 62 degrees and the room is COLD, your in the wrong spot..

for a test, set the FLOOR at 66 and the OVERHEAD at 62...


Edited by steve(ill) - 01 Dec 2024 at 8:20am
Like them all, but love the "B"s.
Back to Top
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Posted: 02 Dec 2024 at 11:09am
Jay, the floor has 4 250' zones with 1 pump and a wall mount thermostat. The commercial built OH box has a 'radiator' about small car size, fan with shroud, 5 louvers and has a pump and wall mounted thermostat right under the box. The system was new a year ago but until more recently the building lacked insulation and a fair 'test' of what worked the best wasn't really possible. I just re-discovered the water pumps have an adjustable speed so that opens new possibilities. 
My goal has been to get the heater to cycle and not run constantly. Right now I have both 'sides' set at 66 which has the heater cycling. I should be able to increase my 'MPG' by playing with the water pump speed. The water temp is now set at 130. 
12 years ago when we put the floor together I cast a piece of tubing sideways into the form for a thermostat that would measure the temp of the slab. My plumber set me up with two wall mount thermostats when he put the Navia in. IDK what is right or wrong but the temp feels consistent between the two bldgs. 
There is so much adjustment with the system, fan speed, pump speeds, 4 zone restriction valves, water temp, thermostat settings and maybe more I haven't figured out. Just since I have been sitting here I have realized I need to check the pump speed settings and should get a temp of the floor surface. 
I appreciate all your thoughts.




Back to Top
jaybmiller View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: Greensville,Ont
Points: 24335
Post Options Post Options   Thanks (0) Thanks(0)   Quote jaybmiller Quote  Post ReplyReply Direct Link To This Post Posted: 02 Dec 2024 at 11:56am
You really should get rid of the wall mounted thermostat for the floor and put one in the floor (which you did install the tubing). I'd also install thermometers in each of the 4 return lines as well as the common feed. Those will show you how much heat is actually going into the floor and which 'zone'.
Nowadays there's LOTS of info about this,especially say 'PEX' suppliers. It IS complicated BUT if you measure and record, you will be able to 'dial in' to get the most consistent heat for the fewest bucks. It's the little 'details' , like a zone next to the big outside door needs more flow to keep that area warm. Obvious to some but NOT the 'computer' controlling the system. Sounds like you have six zones...2 OH units and 4 in the floor. Each should be monitored and individually controlled. Ideally OH units come on only when humans are there, can be 'setback' when place is empty.
I used to set most of my clients for 70* daytime, 45* after hours. preheat usually took 2 hours(OH units put out a LOT of heat ! ) Online 'tools' can help give you a rough idea based on VOLUME of area, runs of PEX, BTU of overheads...but to fine tune, you'll need to be there or measure the temperatures. If you're storing steel, it acts as a heatsink..slowly warms up, releases at night unlike cardboard boxes ! BTW if warm building is 'mission critical' have some kind of alarm system setup to inform you ! In my case, each zone would report 55*f and 50*f. Allowed me to turn heat on in other zones while HVAC guy got to building to fix busted OH units.
3 D-14s,A-C forklift, B-112
Kubota BX23S lil' TOOT( The Other Orange Tractor)

Never burn your bridges, unless you can walk on water
Back to Top
Tbone95 View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 31 Aug 2012
Location: Michigan
Points: 11964
Post Options Post Options   Thanks (0) Thanks(0)   Quote Tbone95 Quote  Post ReplyReply Direct Link To This Post Posted: 02 Dec 2024 at 12:06pm
Sorry but who cares what the temperature of the floor is? Your goal is usually to make a room feel comfortable ( or at the temperature you want), not to heat a floor to some point.   So measure and control the room. I suppose it might be interesting to see what temperature the floor is at times but I wouldn’t bother with trying to control with a thermostat in the floor. Our house has in floor heat like this for the basement and garage with thermostats on the walls. Works perfect. My niece and her husband and a little child lived in the basement for close to a year including a hard winter. Comfy cozy 0 complaints. The one thing I’ll say, if you are normally comfortable in a 70 degree room, you’ll probably be comfortable at 66-67 in a room with a heated concrete floor.

Edited by Tbone95 - 02 Dec 2024 at 12:08pm
Back to Top
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Posted: 02 Dec 2024 at 1:56pm
JayB I have one overhead heater. The other building has the floor heat.
 The 190k btu 'Nav' I have will run 3 systems and provide domestic hot water so I still have 'room' to add a heat loop thru the lean-to... lol.
I agree about checking temps to dial in the system. I gave the man a check for 3000 gallons of propane this year for the house and shop, winced a bit... Hopefully I fail to use it all and have a huge credit next fall. 


Edited by scott - 05 Dec 2024 at 8:02am
Back to Top
tadams(OH) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 17 Sep 2009
Location: Jeromesville, O
Points: 10609
Post Options Post Options   Thanks (0) Thanks(0)   Quote tadams(OH) Quote  Post ReplyReply Direct Link To This Post Posted: 02 Dec 2024 at 1:57pm
Tbone is right you don't set on the floor you want the temperature to be what is confortable at the level you are working.
Back to Top
DonBC View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 12 Sep 2009
Location: Courtenay, BC,
Points: 930
Post Options Post Options   Thanks (0) Thanks(0)   Quote DonBC Quote  Post ReplyReply Direct Link To This Post Posted: 02 Dec 2024 at 3:32pm
For a couple of small shops I have designed a couple of systems using a domestic hot water tank as the heat source for in-floor heating.
Jack of all trades, master of none
Back to Top
DaveKamp View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 12 Apr 2010
Location: LeClaire, Ia
Points: 5957
Post Options Post Options   Thanks (0) Thanks(0)   Quote DaveKamp Quote  Post ReplyReply Direct Link To This Post Posted: 02 Dec 2024 at 10:32pm
First thing I would do... is some temporary rearangement of piping connections.

Come out of the overhead liquid-to-air heater, and pipe that into your floor circuits.

As others noted, the 20F drop is more relevant than the ambient air temperature and your water heater's temperature setpoint.  The 'drop' determines how much thermal transfer is occurring.

The water heating unit will take the incoming water, and raise it by a certain number of degrees based on two things-  First is the FLOW RATE (flow faster, and temp rise will be less), and second is the cutoff temperature of the heater (hit the cutoff temp, and the heater will stop itself).

Likewise, the overhead cooling unit will take the incoming water at a certain temperature, and lower that water by a certain number of degrees based on two things-  first being the Flow Rate (which is set by your pump sizing, plumbing flow restriction and pump speed, if adjustable) and the cooling area and coefficient (the 'radiator's surface area and ability to transfer thermal energy).

The faster you flow water, the less the heating side will heat, and the less the radiating side will radiate, so your medium (liquid) temperature will fall.  Slow it down too slow, and the medium temperature will rise at the heating side, and fall at the cooling side.  You want a happy midpoint, which is why hydronic heat guys constantly measure, calculate flow, and make adjustments to get 'balance'.

Back to what I said-  Flow through the overhead, then into the slab.  This is what I'd do first, because that overhead is giving you a 20 degree drop, the slab will give you another 20-30 degree drop when the building is cold, but you'll be warming the most critical of the 'comfort zone' of your building.

What does Dave mean by that?  Well, look at the others' notes from above-  the overhead radiator is taking air that is above your head, and raising it's temperature, so that heat rises.  Where are you standing?  Hint-  You're not standing on the ceiling... and warm air on the ceiling warms the roof, NOT your feet, and not the air at shoulder level and down.

By taking the outlet of the radiant and piping it through the floor, you're getting additional energy pushed into that massive chunk of man-made rock to get it up to some point that doesn't cause you chilled toes, soles, arches, ankles, shins, knees, thighs... in a gradual rise... thus, your comfort actually improves.  Warm air, even at head level, means NOTHING when your piggies won't move, and your calves and knees ache.  Get that floor warm, and your whole body will feel better, even if the air temp at face level is 50F.

In short, blowing hot air down is a short-term comfort.  Getting that slab up to temp is where the real benefit starts.   Once it's all warm, THEN consider your flow path and circumstance.

Finally-  Trying to get a system to 'cycle' is not a sensible goal.  Running constant, at a rate which matches heat loss, is the goal... the only operating variation you'd ever expect, is that which occurs when you 1) open an overhead door  or 2) go from day to night, and night to day.   Once you've gotten the volume to your target climate-controlled temperature, your building's insulation properties are doing all the 'work'.  Your energy input will, at that point, equate to what is lost through the 'insulation' perimeter, and that perimeter's thermal loss will have only three variables in play-  first is temperature difference from inside to outside, and the second is thermal gain from solar (incoming sunlight), and the last is changeover losses (from air while doors open, or when you bring in something cold to warm up).

This all being said, it IS possible to have a floor that gets 'too hot', but it sounds like the OP is WAY FAR from that.  I've had some floors so warm that one cannot WALK on them comfortably for more than a minute or two.  Be this as it may, having 120f water flowing through the floor does NOT mean that the FLOOR is 120f... it'd take several weeks of 120f water flowing through a 6" insulated slab to accept, and transfer enough energy to warm a slab from say... 35F to over 75F.  IF the slab is 75F, and the thermostat in the room is at 70, the ONLY way the thermostat would command more heat, would be because the AIR temp is still below 70F.  A 75F slab will change that right quick once the overhead door is closed and all the ice and snow on that old truck has thawed out and melted away.  

I have thermo sensors in my slabs-  I poured in blind-ended pieces of PEX specifically so I could push in sensors to monitor slab temp.  I don't use them to control anything at THIS TIME, but eventually I'll have monitoring hardware, and when I do, I'll probably put in a function that causes the slab circuit to get bypassed whenever it is already above say... 79F or so.  Any warmer than that, and I can't lay on the floor and twist wrenches.


Edited by DaveKamp - 02 Dec 2024 at 10:40pm
Ten Amendments, Ten Commandments, and one Golden Rule solve most every problem. Citrus hand-cleaner with Pumice does the rest.
Back to Top
DougG View Drop Down
Orange Level
Orange Level


Joined: 20 Sep 2009
Location: Mo
Points: 8246
Post Options Post Options   Thanks (0) Thanks(0)   Quote DougG Quote  Post ReplyReply Direct Link To This Post Posted: 03 Dec 2024 at 8:18am
One thing about heating concrete floors is set it at a temp and let it do its thing, - had that in my shop, 65 seemed to be just right
Back to Top
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Posted: 03 Dec 2024 at 10:27am
Dave,
I question my own wording but when I said I wanted the system to cycle I mean I want the water heater to get a break every now and again. Liken it to your house furnace running 24-7. 

I went all fall putting on the overhead for a couple hours and letting it heat both sides. More recently the overhead box was let run 24-7 but when outside temps dropped into the 20s with 20 MPH wind the OH box would not keep up (see above). At that point the water heater was running constantly.

Per the suggestion above I turned on the floor to see if it would help the OH box keep up. I set both thermostats at 66 and have not touched them since. At this point the water heater appears to be running about half the time, you can watch the 'Heat On' light on the thermostats go on and off. 

I like the idea of adding some floor heat to the loop that contains the overhead box. Maybe that is where the hot water for the lean to floor comes from should that day ever come... 
Thank You for your thoughts.
Back to Top
SyncPil View Drop Down
Bronze Level
Bronze Level
Avatar

Joined: 28 Oct 2024
Location: Denver
Points: 12
Post Options Post Options   Thanks (0) Thanks(0)   Quote SyncPil Quote  Post ReplyReply Direct Link To This Post Posted: 04 Dec 2024 at 6:26am
Interesting thread i must say!!
Running both systems together is likely more efficient, as radiant floor heat provides consistent warmth and reduces the load on the overhead box. Lower the water temp to around 120°F-130°F and use both. The floor heat will help maintain overall warmth, and the overhead can handle any extra demand.
Back to Top
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Posted: 04 Dec 2024 at 11:34am
Steve I turned down the overhead to 62 and left the floor at 66 last night. This morning the thermostats read 62 and 66 and neither had the "heat on" light lit.Clap
Back to Top
steve(ill) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 11 Sep 2009
Location: illinois
Points: 85476
Post Options Post Options   Thanks (0) Thanks(0)   Quote steve(ill) Quote  Post ReplyReply Direct Link To This Post Posted: 04 Dec 2024 at 12:25pm
sounds like your making progress... What is that ambient outside temp ?   ..... i might have missed it, but WHERE is the thermostat for the floor heat ?  In the same building with the overhead radiator ?? ... from the discussion i assumed the two thermostats are both in the same location .

Edited by steve(ill) - 04 Dec 2024 at 12:30pm
Like them all, but love the "B"s.
Back to Top
DonBC View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 12 Sep 2009
Location: Courtenay, BC,
Points: 930
Post Options Post Options   Thanks (0) Thanks(0)   Quote DonBC Quote  Post ReplyReply Direct Link To This Post Posted: 04 Dec 2024 at 2:07pm
About five years ago I was dragged out of retirement to engineer a unique in-floor heating system for a new elementary school for a religious group. They wanted in-floor heating as the children would be spending a lot of time on the floor. There were no engineers in the area that had designed in-floor heating systems. The secret to the system was a special thermostat designed for in-floor heating systems. It had two sensors, one measured slab temperature to prevent damage to the concrete from over heat and a second sensor measured room temperature. The last challenge was to educate the staff how to use the thermostat as in-floor system has a very slow response time compared to a forced air system.
Jack of all trades, master of none
Back to Top
scott View Drop Down
Orange Level Access
Orange Level Access


Joined: 12 Sep 2009
Location: michigan
Points: 2681
Post Options Post Options   Thanks (0) Thanks(0)   Quote scott Quote  Post ReplyReply Direct Link To This Post Posted: 05 Dec 2024 at 9:05am
It had been in the 30s for a week last year when they installed the heater. The whole building, two shops, had been heated with a woodstove previously. Knowing the heater was coming I got lazy about fetching firewood and the floor on the radiant heat side was cold... it took 3 days to get the slab warmed up. On the second day you could feel it starting to take the edge off the cold, I was bummed thinking that was it... then I got out to the shop the 3rd day and had T-shirt conditions and the joy returned. I had figured it was going to be what it was on the second day, wrong.
This year I had been using the water heater to run just the overhead box which was enough to keep the slab pre- warmed up. I think the floor was done heating up in a day or so. 
Last night the floor side thermostat read 66 and the OH box side was set to 62. Experimenting, I kicked up the 62 to 68. The OH box got it up to 66 quickly but it never got to 68, seems after 66 it has to raise the temp throughout the whole building to gain the extra 2 degrees??


Back to Top
steve(ill) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 11 Sep 2009
Location: illinois
Points: 85476
Post Options Post Options   Thanks (0) Thanks(0)   Quote steve(ill) Quote  Post ReplyReply Direct Link To This Post Posted: 05 Dec 2024 at 9:37am
thats what i was thinking Scott... IF your two thermostates are measuing AIR TEMP on th wall near the radiator box unit, then when you set the hot air unit ABOVE the floor heater unit, the air gets warm and shuts off hot water to the FLOOR heater........ I think you set the FLOOR heater where you want it because it is slow reacting ( maybe 66 degrees)... And set the radiator unit at 62 to keep it "ok to work"... and if you want more instant heat, you just tern the radiator unit up while you are working.......... but 62 should be GREAT for most working conditions......
Like them all, but love the "B"s.
Back to Top
tadams(OH) View Drop Down
Orange Level Access
Orange Level Access
Avatar

Joined: 17 Sep 2009
Location: Jeromesville, O
Points: 10609
Post Options Post Options   Thanks (0) Thanks(0)   Quote tadams(OH) Quote  Post ReplyReply Direct Link To This Post Posted: 05 Dec 2024 at 12:26pm
You need some ceiling fans to move the heat down from the ceiling. If you don't the heat will rise and never get circulate.