This site is not affiliated with AGCO Inc., Duluth GA., Allis-Chalmers Co., Milwaukee, WI., or any surviving or related corporate entity. All trademarks remain the property of their respective owners. All information presented herein should be considered the result of an un-moderated public forum with no responsibility for its accuracy or usability assumed by the users and sponsors of this site or any corporate entity.
The Forum Parts and Services Unofficial Allis Store Tractor Shows Serial Numbers History
Forum Home Forum Home > Allis Chalmers > Farm Equipment
  New Posts New Posts
  FAQ FAQ  Forum Search   Events   Register Register  Login Login


Gleaner M2 A/C questions

 Post Reply Post Reply
Author
Message
Bird76Mojo View Drop Down
Silver Level
Silver Level


Joined: 12 Mar 2015
Location: Illinois
Points: 221
Post Options Post Options   Thanks (0) Thanks(0)   Quote Bird76Mojo Quote  Post ReplyReply Direct Link To This Post Topic: Gleaner M2 A/C questions
    Posted: 08 Sep 2019 at 1:53am
My dad has a M2 Corn and Soybean Special that we're working on the A/C system.. The previous technician that came by just seemed to add more refrigerant to the system and it worked for about a day or two. I own enough diagnostic tools to figure this out but I need help.

Today I hooked up the A/C gauges to the system (after thoroughly cleaning the condenser and evaporator) and the system pressures are equal on both the low and high sides.. They were also extremely high. Both sides were around 80-85psi, which isn't normal.. It's an extremely old system so I do expect leaks.

I'm just wondering what components could be bad.

The compressor clutch wouldn't kick on, so I ran a jumper wire bypassing the high and low pressure switches, and the A/C clutch did engage, but the system never got even remotely cold. I let out refrigerant out and I added more, trying to get the system to actuate the A/C clutch, but it wouldn't engage without me jumpering the high/low pressure switches.

I'm thinking the expansion valve isn't regulating the system pressures since reducing system pressures and/or adding more refrigerant didn't improve anything, but I'm not sure on any of it, so any advice is appreciated.. 

I did verify that the heater control valve is closing off the flow of coolant, and the A/C compressor clutch is activating when I jumper the low/high pressure switches.

No obvious leaks are present when looking for refrigerant oil around all components..


GB :)
Back to Top
Sponsored Links


Back to Top
Pete from IL View Drop Down
Silver Level
Silver Level


Joined: 29 Dec 2009
Location: Beecher IL.
Points: 311
Post Options Post Options   Thanks (0) Thanks(0)   Quote Pete from IL Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 6:55am
What did the pressures do when you got the compressor clutch to activate? The high side pressure should have gone up. If not then your compressor is not pumping anything.
Back to Top
MACK View Drop Down
Orange Level
Orange Level


Joined: 17 Nov 2009
Points: 7664
Post Options Post Options   Thanks (0) Thanks(0)   Quote MACK Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 8:00am
I would say expansion valve is bad. Replace expansion valve and receiver drier, pull a vacuum, and recharge.        MACK
Back to Top
Bird76Mojo View Drop Down
Silver Level
Silver Level


Joined: 12 Mar 2015
Location: Illinois
Points: 221
Post Options Post Options   Thanks (0) Thanks(0)   Quote Bird76Mojo Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 12:40pm
After I got the compressor clutch to engage by bypassing both safety switches, the pressures never changed. They stayed equal on both the high and low side, at static pressure. The same as when the system wasn't running.

I was thinking the expansion valve was bad myself, and it's not regulating refrigerant flow rates in the system.

Now I'll have to find the part numbers for the expansion valve and receiver dryer..


Thanks for the replies fellas.

Edited by Bird76Mojo - 08 Sep 2019 at 12:41pm
Back to Top
tbran View Drop Down
Orange Level
Orange Level


Joined: 14 Sep 2009
Location: Paris Tn
Points: 3526
Post Options Post Options   Thanks (0) Thanks(0)   Quote tbran Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 3:13pm
Evidently you have a multitude of issues.  First IF the system had 80 # - you have a bad low pressure or high pressure valve.  The low pressure opens  and breaks the circuit at say 30# ish  and the high side will open at the high 300's depending on valve.  80# is about right equaled on a hot day.  When the clutch engaged you should have seen some difference in pressure even if the valve is stuck open.  Unless the hoses have been replaced with barrier hoses R134 will seep out the hoses and a small recharge will be necessary probably every 30 60 days.  IF the unit has been sitting - the compressor shaft seal will probably be seeping as well.  The other issue is the condenser core - almost all the ones I have ever seen need about an hour of pressure washing - really - they may look clean .. but... If you do not have a strong air flow from the cab blower - it is probably clogged as well.  A dirty  condenser will cause high pressure and a dirty evaporator will freeze over.   As stated , change the drier and expansion valve , pull a vacuum for at least 15 minutes,  let it set for at least 10 minutes to check for a leak - it probably will leak at the fittings from the high side hose fitting crimps - grab them and twist to see if they are loose.  Many times the system will hold a vacuum then leak under pressure at these places.   Charge the system with liquid  until it will hold no more, then turn the can or cans to vapor to finish the charge when the compressor kicks on. Don't listen to anyone about pounds of charge - go by pressures.  The high side on a 80-90 degree   should be 225 PSI -  + or - 10 psi.  The low side must be below 20 psi to be cold.  Do the charge with the fan on high.  Then shut off the recirculation lever to max recirculation and turn the fan on low with door shut - the low pressure should drop to 10 to 12 psi and the thermostat should click the clutch out.   IF you see the clutch clicking on the off - it is overcharged or a bad HP switch.  The fans on the condenser core should be on when the compressor is on.  I have seen a few units where the  thermostat wire is trying to run the compressor and fans - this will not work.  The thermostat wire only triggers and relay that powers both fans and clutch.  Hope this heals and helps.     
When told "it's not the money,it's the principle", remember, it's always the money..
Back to Top
critter View Drop Down
Silver Level Access
Silver Level Access


Joined: 13 Nov 2013
Location: Ohio
Points: 254
Post Options Post Options   Thanks (0) Thanks(0)   Quote critter Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 3:49pm
If the pressures didn't change with the clutch engaged, the compressor is bad.
Back to Top
Bird76Mojo View Drop Down
Silver Level
Silver Level


Joined: 12 Mar 2015
Location: Illinois
Points: 221
Post Options Post Options   Thanks (0) Thanks(0)   Quote Bird76Mojo Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 6:50pm
The system worked last year and the local Allis technician came by and hooked up his gauges to the system and ended up adding more R134a to it.. According to my father, it wasn't the coldest but it was acceptable.

Low or high pressure valve? You mean "switches" surely.. 

I suppose I could try lowering the system pressure to below 30psi to see if the compressor will kick-on all on it's own, without bypassing the low/high pressure switches, but when I lowered the system pressures last time, both sides dropped equally and stayed equal while it was running.

I have already cleaned the condenser and it's as spotless as it can be. With the switches bypassed to make the compressor and the condenser fans run, it will easily hold a piece of cardboard against the outside of the condenser box mesh screen.. So I'm getting plenty of air flow through the condenser.

I also took apart the panels in the cab and checked everything was clean around the evaporator, and the cabin air filter is pretty new and not dirty.

The heater valve is working nicely and shutting off hot coolant flow as well.

As far as I know, the system could have so much humidity and outside air in it that it can't condense it, and that could be why the gauges don't show different pressures on either side. Non-condesables.. This is the part I'm not sure on and lack the proper knowledge. Why the gauges are reading equal pressures..

I hate to be throwing parts at it until it's fixed. I do know that the receiver-dryer should be replaced if I open the system for other work, so I'm okay with doing that. It's only $25 and the expansion valve seems to cost about the same, but I hate to be spending my fathers money needlessly..

Edited by Bird76Mojo - 08 Sep 2019 at 6:51pm
Back to Top
critter View Drop Down
Silver Level Access
Silver Level Access


Joined: 13 Nov 2013
Location: Ohio
Points: 254
Post Options Post Options   Thanks (0) Thanks(0)   Quote critter Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 7:13pm
System pressure is always equal when a system is off (compressor doing nothing). In my opinion you have atleast 2 different problems
1 clutch won't engage. (bad wire, bad pressure switches, bad fuse, something electrical)
2 compressor is likely bad
Back to Top
MACK View Drop Down
Orange Level
Orange Level


Joined: 17 Nov 2009
Points: 7664
Post Options Post Options   Thanks (0) Thanks(0)   Quote MACK Quote  Post ReplyReply Direct Link To This Post Posted: 08 Sep 2019 at 7:27pm
CHANGE THE EXPANSION VALVE.      MACK
Back to Top
Bird76Mojo View Drop Down
Silver Level
Silver Level


Joined: 12 Mar 2015
Location: Illinois
Points: 221
Post Options Post Options   Thanks (0) Thanks(0)   Quote Bird76Mojo Quote  Post ReplyReply Direct Link To This Post Posted: 19 Sep 2019 at 7:38pm
We had a technician come by today and he checked the pressures and said it was empty, which is odd because it held pressure all year just fine. Then he ended up pressurizing the system with nitrogen. We found a leak where the line hooked to the dryer/accumulator, so he put a new o-ring in that connection and it sealed up ok. Then we found two hoses had several large bubbles/warts on them, so we removed them and capped off the hose connections at the cab, and closed the service valves on the compressor.

So I'm in the process of making new hoses now. We had the technician call and price the hoses and the two of them that run from compressor/condenser to the outside connection at the cab/steps were over $500. I already had 90ft of #6, #8, and #10 hose laying around from a custom hotrod A/C system I built, and the A/C fitting crimping tool, so it's worth a shot.. So I went and bought $40 worth of Gates A/C beadlock fittings today.

We'll make the hoses tomorrow and go from there.
Back to Top
wekracer View Drop Down
Orange Level
Orange Level
Avatar

Joined: 13 Oct 2009
Location: Tebbetts, MO
Points: 1590
Post Options Post Options   Thanks (0) Thanks(0)   Quote wekracer Quote  Post ReplyReply Direct Link To This Post Posted: 20 Sep 2019 at 4:05pm
This may be a dumb question but did you open the valves on the compressor when you put your gauges on. If not you may have been seeing the pressure that was still on your hoses depending on what fittings you have.
Back to Top
Bird76Mojo View Drop Down
Silver Level
Silver Level


Joined: 12 Mar 2015
Location: Illinois
Points: 221
Post Options Post Options   Thanks (0) Thanks(0)   Quote Bird76Mojo Quote  Post ReplyReply Direct Link To This Post Posted: 20 Sep 2019 at 5:42pm
No, I had the service valves open. But I do think I might have accidentally cracked open the manifold gauge valve on the low side when I originally checked it out..

I got the new A/C hoses built today, installed and secured in place. I put a vacuum on it for about 10 minutes and then closed the manifold gauge valves to see if it would hold vacuum. It held perfectly for about an hour.. So I turned the vacuum pump back on and let it run in two 30 minute cycles with 30 minutes of rest in between for the vacuum pump to cool down a little..

We're going to see if it will hold vacuum overnight. It's held perfectly for about 2 hours now. So time will tell..

The next hurdle will be getting the compressor to kick on as I'm adding refrigerant to the low side. It's looking like I'm going to have to bypass each of the pressure switches one at a time until I figure out which one is defective, but we'll find out once we start adding refrigerant.

The good thing so far is that dad has only invested $40 in A/C hose fittings, because I already had all the A/C barrier hose laying around from my hotrod build, and I already own the A/C hose crimper. So if this all works, we'll have saved over $400 vs buying the hoses from the local AGCO dealer.

To be continued....

Edited by Bird76Mojo - 20 Sep 2019 at 5:43pm
Back to Top
Bird76Mojo View Drop Down
Silver Level
Silver Level


Joined: 12 Mar 2015
Location: Illinois
Points: 221
Post Options Post Options   Thanks (0) Thanks(0)   Quote Bird76Mojo Quote  Post ReplyReply Direct Link To This Post Posted: 21 Sep 2019 at 9:50pm
Well, the system held vacuum overnight perfectly. Zero leakdown. So today I pulled a vacuum again for about 30 minutes and then I hooked up a can of refrigerant. I couldn't get the system to take very much refrigerant at all, so I bypassed the safety switches to make it kick on.

Once I got the compressor running, it was taking in refrigerant easily. After I got it to take 2 cans, we shut everything off and I hooked the safety switches back up to see if the compressor would kick on when we activated the A/C in the cab. We restarted the engine, turned on the A/C, and it kicked on successfully. My fathers friend is a retired A/C mechanic and he recommended to use 4 cans of R134a in the M2, so that's what I put in the system.

After adding 4 full cans, the A/C was colder than either one of my pickup trucks, and they're very good A/C systems that perform flawlessly. Dad and I were both amazed at how cold it is. It will truly freeze you out of the cab in less than a minute. 

We saved ourselves well over $400 compared to buying the A/C hoses from the AGCO dealer and we didn't have to call the service technician back saving dad even more cash..

So, I'm calling this one a WIN for now. Should it need more refrigerant in the future (I'm sure it will at some point even though it leaked zero vacuum) I plan to add one can with the UV dye in it to pinpoint any leaks for repair.


Thanks for all of the advice and assistance y'all. :)