Topic: diesel fuel tanks
Posted By: jaybmiller
Subject: diesel fuel tanks
Date Posted: 16 Jul 2012 at 1:53pm
Had a neighbour ask a question..
seems he's heard that you shouldn't put diesel into a galvanized fuel tank.
 
Anyone else heard of this or know why ???


-------------
3 D-14s,A-C forklift, B-112
Kubota BX23S lil' TOOT( The Other Orange Tractor)

Never burn your bridges, unless you can walk on water



Replies:
Posted By: B26240
Date Posted: 16 Jul 2012 at 3:56pm
I have also heard this but don't know if it's true or not.


Posted By: dave63
Date Posted: 16 Jul 2012 at 5:00pm
Galvanizeing is a zink coating and it can flake off and clog filters, ruin injection pumps, injectors, ect.
You also are not sapposed to use galvinized pipe for the same reason.
We had a  generator set installed at our fire department and the plumber ran galvinized pipe for the fuel lines. after it was in for awhile i decided to read the operators manual in order to properly service it and it states in the book not to use galvinized pipe for this reason.
So far the unit has been oparateing for anout 6 years no problem so far. 


-------------
The universal answer to all questions is yes, how much do you want to spend?


Posted By: DaveKamp
Date Posted: 16 Jul 2012 at 5:40pm
Here's what Page 120 of the Cummins install manual
http://www.cumminspower.com/www/literature/applicationmanuals/t-030_p115-132.pdf  

says:

"Diesel Fuel Piping
Diesel fuel lines should be constructed from black iron pipe.  Cast iron and aluminum pipe and fittings must not be used because they are porous and can leak fuel.  Galvanized fuel lines, fittings, and tanks must not be used because the galvanized coating is attacked by the sulfuric acid that forms when the sulfur in the fuel combines with tank condensate, resulting in debris that can clog fuel pumps and filters.  Copper lines should not be used because fuel polymerizes (thickens) in copper tubing during long periods of disuse and can clog fuel injectors.  Also, copper lines are less rugged than black iron, and thus more susceptible to damage."